Udløserindstillinger til drift med Easy UPS 3M 208 V
Med én batteriafbryderboks E3MBBB60K80H
Med én batteriafbryderboks E3MBBB100K200H
Med to batteriafbryderbokse E3MBBB60K80H
| UPS-klassifikation | Maksimal backuptid på batteri (minutter) | Batteriblokke | Batteristrenge i alt | Batteriafbryder 1 | Batteriafbryder 2 | ||
|---|---|---|---|---|---|---|---|
| Batteristrenge | Ir/Im-indstilling (A) | Batteristrenge | Ir/Im-indstilling (A) | ||||
| 50 kVA |
240 |
32-40 |
5 |
3 |
175/1250 |
2 |
175/1250 |
|
240 |
32-40 |
6 |
3 |
175/1250 |
3 |
175/1250 |
|
|
240 |
32-40 |
7 |
4 |
175/1250 |
3 |
175/1250 |
|
|
240 |
32-40 |
8 |
4 |
175/1250 |
4 |
175/1250 |
|
| 60 kVA |
240 |
32-40 |
5 |
3 |
175/1250 |
2 |
175/1250 |
|
240 |
32-40 |
6 |
3 |
175/1250 |
3 |
175/1250 |
|
|
240 |
32-40 |
7 |
4 |
175/1250 |
3 |
175/1250 |
|
|
240 |
32-40 |
8 |
4 |
175/1250 |
4 |
175/1250 |
|
| 80 kVA |
240 |
32-40 |
5 |
3 |
175/1250 |
2 |
175/1250 |
|
240 |
32-40 |
6 |
3 |
175/1250 |
3 |
175/1250 |
|
|
240 |
32-40 |
7 |
4 |
175/1250 |
3 |
175/1250 |
|
|
240 |
32-40 |
8 |
4 |
175/1250 |
4 |
175/1250 |
|
| 100 kVA |
240 |
32-40 |
5 |
3 |
200/1250 |
2 |
200/1250 |
|
240 |
32-40 |
6 |
3 |
200/1250 |
3 |
200/1250 |
|
|
240 |
32-40 |
7 |
4 |
200/1250 |
3 |
200/1250 |
|
|
240 |
32-40 |
8 |
4 |
200/1250 |
4 |
200/1250 |
|