Trip Settings for Operation with Easy UPS 3L at Power Factor 1.0
With One Battery Breaker Box E3MBBB100K200H
UPS rating 250 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker | |
---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | |||
≤10 |
36-38 |
1-4 |
1-4 |
600/1500 |
≤15 |
40 |
1-4 |
1-4 |
600/1500 |
≤30 |
42 |
1-4 |
1-4 |
600/1500 |
240 |
44-50 |
1-4 |
1-4 |
600/1500 |
UPS rating 300 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker | |
---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | |||
≤5 |
38-42 |
1-4 |
1-4 |
600/1500 |
≤10 |
44-46 |
1-4 |
1-4 |
600/1500 |
≤15 |
48-50 |
1-4 |
1-4 |
600/1500 |
UPS rating 400 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker | |
---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | |||
≤5 |
50 |
1-4 |
1-4 |
600/1500 |
With Two Battery Breaker Boxes E3MBBB100K200H
UPS rating 250 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | ||
---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | |||
240 |
36-50 |
2 |
1 |
420/1500 |
1 |
420/1500 |
240 |
36 |
3 |
2 |
540/1500 |
1 |
420/1500 |
240 |
38-42 |
3 |
2 |
480/1500 |
1 |
420/1500 |
240 |
44-50 |
3 |
2 |
420/1500 |
1 |
420/1500 |
240 |
36-50 |
4 |
2 |
420/1500 |
2 |
420/1500 |
240 |
36-38 |
5 |
3 |
480/1500 |
2 |
420/1500 |
240 |
40-50 |
5 |
3 |
420/1500 |
2 |
420/1500 |
240 |
36-50 |
6 |
3 |
420/1500 |
3 |
420/1500 |
240 |
36 |
7 |
4 |
480/1500 |
3 |
420/1500 |
240 |
38-50 |
7 |
4 |
420/1500 |
3 |
420/1500 |
240 |
36-50 |
8 |
4 |
420/1500 |
4 |
420/1500 |
UPS rating 300 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | ||
---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | |||
240 |
36-38 |
2 |
1 |
480/1500 |
1 |
480/1500 |
240 |
40-50 |
2 |
1 |
420/1500 |
1 |
420/1500 |
240 |
36-40 |
3 |
2 |
600/1500 |
1 |
420/1500 |
240 |
42-44 |
3 |
2 |
540/1500 |
1 |
420/1500 |
240 |
46-50 |
3 |
2 |
480/1500 |
1 |
420/1500 |
240 |
36-38 |
4 |
2 |
480/1500 |
2 |
480/1500 |
240 |
40-50 |
4 |
2 |
420/1500 |
2 |
420/1500 |
240 |
36 |
5 |
3 |
600/1500 |
2 |
420/1500 |
240 |
38-40 |
5 |
3 |
540/1500 |
2 |
420/1500 |
240 |
42-46 |
5 |
3 |
480/1500 |
2 |
420/1500 |
240 |
48-50 |
5 |
3 |
420/1500 |
2 |
420/1500 |
240 |
36-38 |
6 |
3 |
480/1500 |
3 |
480/1500 |
240 |
40-50 |
6 |
3 |
420/1500 |
3 |
420/1500 |
240 |
36-38 |
7 |
4 |
540/1500 |
3 |
420/1500 |
240 |
40-44 |
7 |
4 |
480/1500 |
3 |
420/1500 |
240 |
46-50 |
7 |
4 |
420/1500 |
3 |
420/1500 |
240 |
36-38 |
8 |
4 |
480/1500 |
4 |
480/1500 |
240 |
40-50 |
8 |
4 |
420/1500 |
4 |
420/1500 |
UPS rating 400 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | ||
---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | |||
240 |
36-40 |
2 |
1 |
600/1500 |
1 |
600/1500 |
240 |
42-44 |
2 |
1 |
540/1500 |
1 |
540/1500 |
240 |
46-50 |
2 |
1 |
480/1500 |
1 |
480/1500 |
5 |
36 |
3 |
2 |
600/1500 |
1 |
420/1500 |
10 |
38-40 |
3 |
2 |
600/1500 |
1 |
420/1500 |
15 |
42-44 |
3 |
2 |
600/1500 |
1 |
420/1500 |
30 |
46 |
3 |
2 |
600/1500 |
1 |
420/1500 |
240 |
48-50 |
3 |
2 |
600/1500 |
1 |
420/1500 |
240 |
36-40 |
4 |
2 |
600/1500 |
2 |
600/1500 |
240 |
42-44 |
4 |
2 |
540/1500 |
2 |
540/1500 |
240 |
46-50 |
4 |
2 |
480/1500 |
2 |
480/1500 |
10 |
36 |
5 |
3 |
600/1500 |
2 |
540/1500 |
15 |
38-40 |
5 |
3 |
600/1500 |
2 |
480/1500 |
30 |
42 |
5 |
3 |
600/1500 |
2 |
420/1500 |
240 |
44-50 |
5 |
3 |
600/1500 |
2 |
420/1500 |
240 |
36-40 |
6 |
3 |
600/1500 |
3 |
600/1500 |
240 |
42-44 |
6 |
3 |
540/1500 |
3 |
540/1500 |
240 |
46-50 |
6 |
3 |
480/1500 |
3 |
480/1500 |
15 |
36-38 |
7 |
4 |
600/1500 |
3 |
540/1500 |
30 |
40 |
7 |
4 |
600/1500 |
3 |
480/1500 |
240 |
42-46 |
7 |
4 |
600/1500 |
3 |
480/1500 |
240 |
48-50 |
7 |
4 |
540/1500 |
3 |
420/1500 |
240 |
36-40 |
8 |
4 |
600/1500 |
4 |
600/1500 |
240 |
42-44 |
8 |
4 |
540/1500 |
4 |
540/1500 |
240 |
46-50 |
8 |
4 |
480/1500 |
4 |
480/1500 |
UPS rating 500 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | ||
---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | |||
10 |
36-38 |
2 |
1 |
600/1500 |
1 |
600/1500 |
15 |
40 |
2 |
1 |
600/1500 |
1 |
600/1500 |
30 |
42 |
2 |
1 |
600/1500 |
1 |
600/1500 |
240 |
44-50 |
2 |
1 |
600/1500 |
1 |
600/1500 |
5 |
42-46 |
3 |
2 |
600/1500 |
1 |
480/1500 |
10 |
48-50 |
3 |
2 |
600/1500 |
1 |
420/1500 |
10 |
36-38 |
4 |
2 |
600/1500 |
2 |
600/1500 |
15 |
40 |
4 |
2 |
600/1500 |
2 |
600/1500 |
30 |
42 |
4 |
2 |
600/1500 |
2 |
600/1500 |
240 |
44-50 |
4 |
2 |
600/1500 |
2 |
600/1500 |
5 |
38-42 |
5 |
3 |
600/1500 |
2 |
600/1500 |
10 |
44-46 |
5 |
3 |
600/1500 |
2 |
540/1500 |
15 |
48-50 |
5 |
3 |
600/1500 |
2 |
480/1500 |
10 |
36-38 |
6 |
3 |
600/1500 |
3 |
600/1500 |
15 |
40 |
6 |
3 |
600/1500 |
3 |
600/1500 |
30 |
42 |
6 |
3 |
600/1500 |
3 |
600/1500 |
240 |
44-50 |
6 |
3 |
600/1500 |
3 |
600/1500 |
5 |
36-40 |
7 |
4 |
600/1500 |
3 |
600/1500 |
10 |
42 |
7 |
4 |
600/1500 |
3 |
600/1500 |
15 |
44-46 |
7 |
4 |
600/1500 |
3 |
540/1500 |
30 |
48-50 |
7 |
4 |
600/1500 |
3 |
540/1500 |
10 |
36-38 |
8 |
4 |
600/1500 |
4 |
600/1500 |
15 |
40 |
8 |
4 |
600/1500 |
4 |
600/1500 |
30 |
42 |
8 |
4 |
600/1500 |
4 |
600/1500 |
240 |
44-50 |
8 |
4 |
600/1500 |
4 |
600/1500 |
UPS rating 600 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | ||
---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | |||
5 |
38-42 |
2 |
1 |
600/1500 |
1 |
600/1500 |
10 |
44-46 |
2 |
1 |
600/1500 |
1 |
600/1500 |
15 |
48-50 |
2 |
1 |
600/1500 |
1 |
600/1500 |
5 |
50 |
3 |
2 |
600/1500 |
1 |
480/1500 |
5 |
38-42 |
4 |
2 |
600/1500 |
2 |
600/1500 |
10 |
44-46 |
4 |
2 |
600/1500 |
2 |
600/1500 |
15 |
48-50 |
4 |
2 |
600/1500 |
2 |
600/1500 |
5 |
46-50 |
5 |
3 |
600/1500 |
2 |
540/1500 |
5 |
38-42 |
6 |
3 |
600/1500 |
3 |
600/1500 |
10 |
44-46 |
6 |
3 |
600/1500 |
3 |
600/1500 |
15 |
48-50 |
6 |
3 |
600/1500 |
3 |
600/1500 |
5 |
44-48 |
7 |
4 |
600/1500 |
3 |
600/1500 |
10 |
50 |
7 |
4 |
600/1500 |
3 |
600/1500 |
5 |
38-42 |
8 |
4 |
600/1500 |
4 |
600/1500 |
10 |
44-46 |
8 |
4 |
600/1500 |
4 |
600/1500 |
15 |
48-50 |
8 |
4 |
600/1500 |
4 |
600/1500 |
With Three Battery Breaker Boxes E3MBBB100K200H
UPS rating 500 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | Battery Breaker 3 | |||
---|---|---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | |||
60 | 36-38 | 3 | 1 | 540/1500 | 1 | 540/1500 | 1 | 540/1500 |
240 | 40-50 | 3 | 1 | 540/1500 | 1 | 540/1500 | 1 | 540/1500 |
10 | 36-38 | 4 | 2 | 600/1500 | 1 | 420/1500 | 1 | 420/1500 |
15 | 40 | 4 | 2 | 600/1500 | 1 | 420/1500 | 1 | 420/1500 |
30 | 42 | 4 | 2 | 600/1500 | 1 | 420/1500 | 1 | 420/1500 |
240 | 44-50 | 4 | 2 | 600/1500 | 1 | 420/1500 | 1 | 420/1500 |
60 | 36-38 | 5 | 2 | 600/1500 | 2 | 600/1500 | 1 | 420/1500 |
240 | 40-50 | 5 | 2 | 600/1500 | 2 | 600/1500 | 1 | 420/1500 |
60 | 36-38 | 6 | 2 | 540/1500 | 2 | 540/1500 | 2 | 540/1500 |
240 | 40-50 | 6 | 2 | 540/1500 | 2 | 540/1500 | 2 | 540/1500 |
30 | 36 | 7 | 3 | 600/1500 | 2 | 480/1500 | 2 | 480/1500 |
60 | 36-38 | 7 | 3 | 600/1500 | 2 | 420/1500 | 2 | 420/1500 |
240 | 40-50 | 7 | 3 | 600/1500 | 2 | 420/1500 | 2 | 420/1500 |
60 | 36-38 | 8 | 3 | 600/1500 | 3 | 600/1500 | 2 | 420/1500 |
240 | 40-50 | 8 | 3 | 600/1500 | 3 | 600/1500 | 2 | 420/1500 |
60 | 36-38 | 9 | 3 | 540/1500 | 3 | 540/1500 | 3 | 540/1500 |
240 | 40-50 | 9 | 3 | 540/1500 | 3 | 540/1500 | 3 | 540/1500 |
60 | 36-38 | 10 | 4 | 600/1500 | 3 | 480/1500 | 3 | 480/1500 |
240 | 40-50 | 10 | 4 | 600/1500 | 3 | 480/1500 | 3 | 480/1500 |
60 | 36-38 | 11 | 4 | 600/1500 | 4 | 600/1500 | 3 | 420/1500 |
240 | 40-50 | 11 | 4 | 600/1500 | 4 | 600/1500 | 3 | 420/1500 |
60 | 36-38 | 12 | 4 | 540/1500 | 4 | 540/1500 | 4 | 540/1500 |
240 | 40-50 | 12 | 4 | 540/1500 | 4 | 540/1500 | 4 | 540/1500 |
UPS rating 600 kVA
Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | Battery Breaker 3 | |||
---|---|---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | |||
60 | 36-38 | 3 | 1 | 600/1500 | 1 | 600/1500 | 1 | 600/1500 |
240 | 40-50 | 3 | 1 | 600/1500 | 1 | 600/1500 | 1 | 600/1500 |
5 | 38-42 | 4 | 2 | 600/1500 | 1 | 480/1500 | 1 | 480/1500 |
10 | 44-46 | 4 | 2 | 600/1500 | 1 | 420/1500 | 1 | 420/1500 |
15 | 48-50 | 4 | 2 | 600/1500 | 1 | 420/1500 | 1 | 420/1500 |
10 | 36 | 5 | 2 | 600/1500 | 2 | 600/1500 | 1 | 420/1500 |
15 | 38-40 | 5 | 2 | 600/1500 | 2 | 600/1500 | 1 | 420/1500 |
30 | 42 | 5 | 2 | 600/1500 | 2 | 600/1500 | 1 | 420/1500 |
240 | 44-50 | 5 | 2 | 600/1500 | 2 | 600/1500 | 1 | 420/1500 |
60 | 36-38 | 6 | 2 | 600/1500 | 2 | 600/1500 | 2 | 600/1500 |
240 | 40-50 | 6 | 2 | 600/1500 | 2 | 600/1500 | 2 | 600/1500 |
5 | 36 | 7 | 3 | 600/1500 | 2 | 540/1500 | 2 | 540/1500 |
10 | 38 | 7 | 3 | 600/1500 | 2 | 540/1500 | 2 | 540/1500 |
15 | 40-42 | 7 | 3 | 600/1500 | 2 | 480/1500 | 2 | 480/1500 |
30 | 44 | 7 | 3 | 600/1500 | 2 | 480/1500 | 2 | 480/1500 |
240 | 46-50 | 7 | 3 | 600/1500 | 2 | 420/1500 | 2 | 420/1500 |
15 | 36 | 8 | 3 | 600/1500 | 3 | 600/1500 | 2 | 480/1500 |
30 | 38 | 8 | 3 | 600/1500 | 3 | 600/1500 | 2 | 480/1500 |
240 | 40-50 | 8 | 3 | 600/1500 | 3 | 600/1500 | 2 | 420/1500 |
60 | 36-38 | 9 | 3 | 600/1500 | 3 | 600/1500 | 3 | 600/1500 |
240 | 40-50 | 9 | 3 | 600/1500 | 3 | 600/1500 | 3 | 600/1500 |
10 | 36 | 10 | 4 | 600/1500 | 3 | 600/1500 | 3 | 600/1500 |
15 | 38-40 | 10 | 4 | 600/1500 | 3 | 540/1500 | 3 | 540/1500 |
30 | 42 | 10 | 4 | 600/1500 | 3 | 480/1500 | 3 | 480/1500 |
240 | 44-50 | 10 | 4 | 600/1500 | 3 | 480/1500 | 3 | 480/1500 |
15 | 36 | 11 | 4 | 600/1500 | 4 | 600/1500 | 3 | 540/1500 |
30 | 38 | 11 | 4 | 600/1500 | 4 | 600/1500 | 3 | 480/1500 |
240 | 40-50 | 11 | 4 | 600/1500 | 4 | 600/1500 | 3 | 480/1500 |
60 | 36-38 | 12 | 4 | 600/1500 | 4 | 600/1500 | 4 | 600/1500 |
240 | 40-50 | 12 | 4 | 600/1500 | 4 | 600/1500 | 4 | 600/1500 |