Trip Settings for Operation with Easy UPS 3M 208 V
With One Battery Breaker Kit E3MBBK60K80H
UPS rating | Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings | Ir/Im Setting (A) |
---|---|---|---|---|
50 kVA |
240 |
32-40 |
1/2/3/4 |
200/1250 |
60 kVA |
240 |
32-40 |
1/2/3/4 |
220/1250 |
With One Battery Breaker Kit E3MBBK100K200H
UPS rating | Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings | Ir/Im Setting (A) |
---|---|---|---|---|
80 kVA |
240 |
32-40 |
1/2/3/4 |
420/1500 |
100 kVA |
240 |
32-40 |
1/2/3/4 |
420/1500 |
With Two Battery Breaker Kits E3MBBK60K80H
UPS rating | Max Battery Backup Time (minutes) | Battery Blocks | Battery Strings Total | Battery Breaker 1 | Battery Breaker 2 | ||
---|---|---|---|---|---|---|---|
Battery Strings | Ir/Im Setting (A) | Battery Strings | Ir/Im Setting (A) | ||||
50 kVA |
240 |
32-40 |
5 |
3 |
175/1250 |
2 |
175/1250 |
240 |
32-40 |
6 |
3 |
175/1250 |
3 |
175/1250 |
|
240 |
32-40 |
7 |
4 |
175/1250 |
3 |
175/1250 |
|
240 |
32-40 |
8 |
4 |
175/1250 |
4 |
175/1250 |
|
60 kVA |
240 |
32-40 |
5 |
3 |
175/1250 |
2 |
175/1250 |
240 |
32-40 |
6 |
3 |
175/1250 |
3 |
175/1250 |
|
240 |
32-40 |
7 |
4 |
175/1250 |
3 |
175/1250 |
|
240 |
32-40 |
8 |
4 |
175/1250 |
4 |
175/1250 |
|
80 kVA |
240 |
32-40 |
5 |
3 |
175/1250 |
2 |
175/1250 |
240 |
32-40 |
6 |
3 |
175/1250 |
3 |
175/1250 |
|
240 |
32-40 |
7 |
4 |
175/1250 |
3 |
175/1250 |
|
240 |
32-40 |
8 |
4 |
175/1250 |
4 |
175/1250 |
|
100 kVA |
240 |
32-40 |
5 |
3 |
200/1250 |
2 |
200/1250 |
240 |
32-40 |
6 |
3 |
200/1250 |
3 |
200/1250 |
|
240 |
32-40 |
7 |
4 |
200/1250 |
3 |
200/1250 |
|
240 |
32-40 |
8 |
4 |
200/1250 |
4 |
200/1250 |